how to size the FFU

发布于:2008-01-29 18:19:29 来自:暖通空调/洁净空调系统 [复制转发]
通常有几种方法去算出FFU
1) Base on the room volume and A/C:
Room Vol ×__________A/C=______________CMH (recirculation air )

Recirculation air = _____________nos of the FFU
2330 (1200*1200ceiling type)
OR

Recirculation air = _____________nos of the FFU
1165 (1200*600, ceiling type)

2) Base on the total ceiling area and coverage :

Total ceiling area (M²) = _______________Nos of ceiling board
1.2×1.2(M²)
Coverage for FFU :

Class 1-----------------------------100%
Class10----------------------------50%
Class100--------------------------34%
Class100(test area)------------25%
Class1000-------------------------17%
Class10000-----------------------8%
Class100000---------------------5%

Nos of ceiling board × FFU coverage (%)= Nos of FFU

3) Base on the machine heat load :


V= Q_____________ = ______________________KW = _______________m³/s=________________________CMH
c×p×∆T 1.2×1.006×∆T( - )

• ∆T : on/off coil temperature
• Q: heat load from machine
• CMH: recirculation air
Recirculation air = _____________nos of the FFU
2330 (1200*1200ceiling type)
OR

Recirculation air = _____________nos of the FFU
1165 (1200*600, ceiling type)

全部回复(4 )

只看楼主 我来说两句
  • xiaohu505
    xiaohu505 沙发
    没看明白 来点翻译啊!!
    2008-03-08 16:05:08

    回复 举报
    赞同0
  • 5354575
    5354575 板凳
    啥意思?
    2008-03-07 22:52:07

    回复 举报
    赞同0
加载更多
这个家伙什么也没有留下。。。

洁净空调系统

返回版块

7.33 万条内容 · 432 人订阅

猜你喜欢

阅读下一篇

洁净室层高太底,设计方案求救!

现有一洁净室,总面积约4000平米,分两层,每层2000平米左右,分成90平米左右的小房间(其中还有15平米左右的百级洁净室),洁净室层高2。6米,吊顶内高度只有0.65米,如果设计集中式空气系统,风管太多太大,吊顶内无法敷设??有没有没什么好的方法????急急,各位大哥大姐多多指教呀!如果采用每个房间用一台吊顶式空调箱(带初中效过滤,湿膜加湿,机组余压600Pa),但是厂家又说这样的方案造价太高,而且以后运行维护都很困难???是这样吗???????????????

回帖成功

经验值 +10