土木在线论坛 \ 电气工程 \ 电气资料库 \ 短路电流计算C因子

短路电流计算C因子

发布于:2015-06-01 14:46:01 来自:电气工程/电气资料库 [复制转发]
C Factor of ETAP Short Circuit Current Calculation-IEC Standard
In this group of ETAP, youspecify if the maximum or minimum short circuit current to be calculated andbased on the selection, different c factors will be used to modify sourcevoltage. There are three options available: Max, User-Defined c Factor, andMin. When the Max option is selected, the maximum values for c factor is usedto calculate maximum fault current:





Nominal Voltage Un
Voltage factor c for the maximum fault current calculation
< 1001 V
c Factor = 1.10
1001 to 35000 V
c Factor = 1.10
> 35000 V
c Factor = 1.10
When the User-Defined c Factor option is selected, ETAP uses theuser specified c factor. The ranges for the c factors are as follows:





Nominal Voltage Un
Voltage factor c for the maximum fault current calculation
< 1001 V
c Factor = 0.95 -- 1.10
1001 to 35000 V
c Factor = 1.00 -- 1.10
> 35000 V
c Factor = 1.00 -- 1.10
When the Min. option is selected, the minimum values for c Factor,as defined in IEC 60909 Standard, are used to calculate minimum fault current.





Nominal Voltage Un
Voltage factor c for the maximum fault current calculation
< 1001 V
c Factor = 0.95
1001 to 35000 V
c Factor = 1.00
> 35000 V
c Factor = 1.00
In each case, ETAP calculates ip, I"k, and Ik .

这个家伙什么也没有留下。。。

电气资料库

返回版块

70.15 万条内容 · 725 人订阅

猜你喜欢

阅读下一篇

电机启动分析程序

ETAP电机启动分析 电动机加速分析 静态加速: 假设电机总是能被起动,计算电机起动过程中电机电流、电机功率、母线电压变化曲线。 需要设置的地方:电机铭牌、堵转电流及堵转功率因数、起动类型、负载类型的加速时间。 动态加速: 电机在起动过程中电流、转矩、滑差、功率输入输出的变化曲线都是通过软件复杂的计算过程计算出来的,电机能否起动要看计算结果。 需要设置的地方:电机铭牌、堵转电流及堵转功率因数、电机

回帖成功

经验值 +10