QUESTION OF MOTOR STARTUP

发布于:2004-10-19 17:32:19 来自:电气工程/防雷减灾 [复制转发]
Dear All,

I’m trying to start-up a 10 kV-2 MW motor, with no load. But the protection relay tripped 3 times with "Negative Sequence Overcurrent Protection, I2>". I’ve checked the disturbance records, the voltages are perfect (there is no V2 or Vr), but the I2 is very high (startup current = ~760 A, I2 = ~60 A).

The motor is a new one (manufactured in 2004) and we have ran it several times before. I’ve disabled the "negative sequance protection" and the motor started up normally. I again took the disturbance records, but this time the I2 was too small (~ 20A).

Can anybody tell me why we "sometimes" face the unbalance currents, even there is no load and the supply voltages are perfect? and why sometimes we don’t face this high unbalance current during start up?

(PS: We have done the electrical tests again, both on the motor and the cable feeding the motor; but could not find any abnormal value).

Thanks in advance!

全部回复(4 )

只看楼主 我来说两句
  • leedreamfly
    leedreamfly 沙发
    楼主为何转一篇英文帖子过来呢?莫非想考考本版斑竹的英语水平,呵呵。
    这段文字来自一个国外的电气论坛,英语好的朋友可以去看看,关于这段文字所
    提的问题也有很详细的讨论。
    2004-10-19 18:45:19

    回复 举报
    赞同0
  • nlb
    nlb 板凳
    检查一下 断路器合闸时的三相同期性.
    2004-10-19 18:32:19