请教关于空调箱飘水!

发布于:2006-08-03 16:39:03 来自:暖通空调/暖通资料库 [复制转发]
空调箱的风机将盘管的凝结水带到了风机段,使得风机段保温湿透、开始存水并漫溢出来,造成吊顶损坏,经检查,空调箱的排水已做存水弯,且积水盘内基本没有存水。其他空调箱并没有出现类似问题,且风管与压头均一致,请问到底是什么问题呢??

全部回复(4 )

只看楼主 我来说两句
  • wen13
    wen13 沙发
    1.check wheteher the cooling coil face velocity is too large. for blow-through unit, the velocity difference in face is 25%, draw-through unit is 20%. when to design unit, it is better to use 500fpm face velocity for cooling coil. lower is better but not less than 300fpm.
    2. check the cooling coil height. the requirement of ASHRAE is chilled water cooling coil should not exceed 45". otherwise, you have to use a long drain pan.
    3. the distance between cooling coil and fan should be long enough. larger than the fan wheel.
    2006-09-11 03:42:11

    回复 举报
    赞同0
  • koukaisei
    koukaisei 板凳
    表冷段是在负压段吧?应该是存水弯的水封高度不够造成的。检查一下水封高度有多少。
    2006-08-06 10:49:06

    回复 举报