关于电击防护采用剩余电流动作保护电器RCD,IEC 60364-4-41:2017
Low-voltage electrical installations Part 4 – 41:Protection for safety –Protection against electric shock(低压电气装置 第4-41部分:安全防护 电击防护)4次提到“ 不超过30mA ” RCD的设置要求。
411.1 通则
Where specified, additional protection is provided by a residual current protective device (RCD) with rated residual operating current not exceeding 30 mA in accordance with 415.1.
当有具体规定时,可采用符合415.1条要求的额定剩余电流动作值 不超过30 mA 的剩余电流保护器(RCD)作附加保护措施。
这条要求又转到415.1部分,该部分为附加保护:剩余电流动作保护电器(RCD)。
411.3.3 用于插座和户外移动式设备的供电更进一步的要求
Further requirements for socket-outlets and for the supply of mobile equipment for use outdoors
Additional protection by means of a residual current protective device (RCD) with a rated residual operating current not exceeding 30 mA shall be provided for
a.c. socket-outlets with a rated current not exceeding 32 A that are liable to be used by ordinary persons and are intended for general use; and
a.c. mobile equipment for use outdoors with a rated current not exceeding 32 A.
额定动作电流 不超过30mA 的剩余电流保护器(RCD)作为附加保护用于:
——供一般人员用普通用途的额定电流不超过32A的交流插座,和
——供户外额定电流不超过32A的交流移动式设备。
此规定在《建筑电气及智能化通用规范》GB 55024-2022第4.6.5条第1、2款有所体现。
411.3.4 在TN和TT系统中用于灯具回路的附加要求
Additional requirements for circuits with luminaires in TN- and TT-systems
In premises designed to accommodate a single household, additional protection by a residual current protective device (RCD) with a rated residual operating current not exceeding 30 mA shall be provided for a.c. final circuits supplying luminaires.
对于单独住户的房屋向灯具供电的交流终端回路,应提供额定剩余动作电流 不超过30mA 的剩余电流保护器。
此部分规定吸收在《建筑电气及智能化通用规范》GB 55024-2022第4.5.4条,即当采用交流供电的正常照明,其灯具安装高度不大于2.5m时,应设RCD作为附加防护。
415.1.1 在交流系统内装设额定剩余电流 不大于30 mA 的RCD,用以在基本防护失效和/或故障保护或用电不慎时的附加保护措施。
The use of RCDs with a rated residual operating current not exceeding 30 mA , is recognized in a.c. systems as additional protection in the event of failure of the provision for basic protection and/or the provision for fault protection or carelessness by users.
综上所述,用于保护人身安全的电击防护,RCD的额定剩余电流动作值都不应大于30mA。